Ted, how was the motor originally connected to the contactors? How
could you possibly determine wye/delta from ohm-meter measurements
when wye and delta circuits are electrically equivalent?
Actually, the resistance measurements for wye connection would be approx.
double that of a delta connection within the motor. If the motor's internal
connection, or winding connection via and external terminal block, etc., is a
delta delta which is two delta configurations in parallel then the single wye
would be 4 times that of the delta delta.

Now, to figure out the correct "phasing" connections of the internal windings
is a bit more complicated and requires the use of a voltmeter and a 6 or 12
volt battery.

Randy Abernathy


[Non-text portions of this message have been removed]

Discussion Thread

cnc002@a... 2003-12-25 15:34:12 UTC Re: [CAD_CAM_EDM_DRO] Re: VFD drive problems with older 3-phase motors (corre... Ted Inoue 2003-12-25 16:56:43 UTC Re: VFD drive problems with older 3-phase motors (corre... vavaroutsos 2003-12-25 17:39:22 UTC Re: VFD drive problems with older 3-phase motors (corre... cnc002@a... 2003-12-25 18:24:58 UTC Re: [CAD_CAM_EDM_DRO] Re: VFD drive problems with older 3-phase motors (corre... cnc002@a... 2003-12-25 18:32:33 UTC Re: [CAD_CAM_EDM_DRO] Re: VFD drive problems with older 3-phase motors (corre... cnc002@a... 2003-12-25 18:37:18 UTC Re: [CAD_CAM_EDM_DRO] Re: VFD drive problems with older 3-phase motors (corre... Bob Muse 2003-12-25 20:27:30 UTC Re: VFD drive problems with older 3-phase motors (corre...