Re: Transformers 3 phase power calculations and fuse size
Posted by
cnc_4_me
on 2005-04-25 15:58:10 UTC
--- In CAD_CAM_EDM_DRO@yahoogroups.com, gary <garyclick1@c...> wrote:
do a 3 phase power calculation I had to look it up.
Since we talk about 3 phase power transformers here from time to time
I will do a few calculations here. For those of you that already
know this please check my work.
In 3 phase we can not just multiply amps x volts like single phase we
have to use the square root of 3 in our formula.
Power in VA = Amps x volts x 1.732
Using the numbers above.
800A x 480V x 1.732 = 665088 VA or 665KVA
Lets assume 90% efficiency of transformer.
.9 x 665KVA = 598KVA, this should power our 560KVA welder nicely.
Let's try one practical example for the types of things we are doing
here in CCED. There have been many discussions about power supplies
for Bridgeport size mills here. The power supplies talked about have
ranged in size from 750VA to 1500VA. Let's pick 1000VA or 1KW and
make a few calculations.
We have 1KVA transformer wired for 220V primary and it has a 56V
secondary.
We want to know the following.
1) Primary current.
2) Secondary current.
3) Fusing recommendations.
Our original formula. Power in VA = Amps x volts x 1.732.
Rearranging we get. Amps = VA/Volts x 1.732.
Primary current = 1000VA / (220V x 1.732) = 2.62A
Secondary current = 1000VA / (56V x 1.732) = 10.3A
Let's add our fudge factor here to make these numbers a little more
realistic. Once again we will assume a 90% efficiency factor. This
number is only applied to the primary.
2.62A primary x 1.1 = 2.88A corrected primary current.
One important point to remember here is we have calculated the
current for each winding. A 3 phase transformer has 3 input windings
and 3 output windings.
Now we need to calculate the fusing requirements for the transformer.
Electrical Code Article 450-3(b) states that each transformer 600
volts, nominal or less, shall be protected by an individual
overcurrent device on the primary side, rated or set at not more than
125% of the rated primary current of the transformer. Where the
primary current of a transformer is 9 amps or more and 125% of this
current does not correspond to a standard rating of a fuse or
nonadjustable circuit breaker, the next higher standard rating shall
be permitted. Where the primary current is less than 9 amps, an
overcurrent device rated or set at not more than 167% of the primary
current shall be permitted. Where the primary current is less than 2
amps, an overcurrent device rated or set at not more than 300% shall
be permitted.
Electrical Code Article 450-3(b)(2) states if a transformer 600 v,
nominal, or less, having a an overcurrent device on the secondary
side rated or set at not more than 125% of the rated secondary
current of the transformer shall not be required to have an
individual overcurrent device on the primary side if the primary
feeder overcurrent device is rated or set at a current value not more
than 250% of the rated primary current of the transformer.
Electrical Code Article 450-3(b)(2) states that a transformer 600 v,
nominal, or less, shall be protected by an individual overcurrent
device on the secondary side, rated or set at not more than 125% of
the rated secondary current of the transformer. Where the secondary
current of a transformer is 9 amps or more and 125% of this current
does not correspond to a standard rating of a fuse or nonadjustable
circuit breaker, the next higher standard rating shall be permitted.
Where the secondary current is less than 9 amps, an overcurrent
device rated or set at not more than 167% of the secondary current
shall be permitted.
What I get out of these codes is that for our example we have to fuse
the primary and do not have to fuse the secondary. Furthermore our
primary fusing can be as high as 167% of primary current ratting.
For our example 167% of 2.88A = 4.8A fuse maximum per winding. I
would say our minimum fuse size should be 125% to give us a little
safety margin. 125% of 2.88A = 3.6A.
Looking in a Bussman fuse catalog it looks like a FRN-R fuse is
suitable. It is rated for 250V and has moderate inrush capability to
allow the capacitor bank to charge up. The FRN-R has the following
sizes in the range we want. 4A and 4.5A, and once again each leg of
the 3 phase transformer should be fused, for a total of 3 fuses.
Picking the proper fuse for the proper job can be tricky. A 4A fuse
of one style will not behave the same as another style 4A fuse. I
would like to see a good write up on proper fuse selection if anyone
knows of one.
References.
Website were I found 3 phase power calculations and NEC electrical
code info.
http://www.elec-toolbox.com/usefulinfo/xfmr-3ph.htm
Bussman fuse catalog.
http://www.bussmann.com/shared/library/catalogs/FullLine_Cat.pdf
Wally
it if you have trouble.
there, for OT subjects, that are not allowed on the CCED list.
> Wally,volts
>
> Our Flash Butt Welder secondary transformer is 140,000Amps at 4
> or 560KVA. In the weldering process this transformer is placed in adead
> short across the work piece (hence the term flash). The incomingservice
> is 480VAC /3P @ 800 Amps. This transformer is controlled andswitched by
> by 12 Water Cooled SCR's and is connected to a 30 Ton Water Chillerto
> prevent a meltdown..and 100
>
> Two other Heat Treating machines have 1300 KVA Transformer Tanks
> Ton Water Chillers.Darn it, you made me think! It has been so many years since I had to
>
> gary
do a 3 phase power calculation I had to look it up.
Since we talk about 3 phase power transformers here from time to time
I will do a few calculations here. For those of you that already
know this please check my work.
In 3 phase we can not just multiply amps x volts like single phase we
have to use the square root of 3 in our formula.
Power in VA = Amps x volts x 1.732
Using the numbers above.
800A x 480V x 1.732 = 665088 VA or 665KVA
Lets assume 90% efficiency of transformer.
.9 x 665KVA = 598KVA, this should power our 560KVA welder nicely.
Let's try one practical example for the types of things we are doing
here in CCED. There have been many discussions about power supplies
for Bridgeport size mills here. The power supplies talked about have
ranged in size from 750VA to 1500VA. Let's pick 1000VA or 1KW and
make a few calculations.
We have 1KVA transformer wired for 220V primary and it has a 56V
secondary.
We want to know the following.
1) Primary current.
2) Secondary current.
3) Fusing recommendations.
Our original formula. Power in VA = Amps x volts x 1.732.
Rearranging we get. Amps = VA/Volts x 1.732.
Primary current = 1000VA / (220V x 1.732) = 2.62A
Secondary current = 1000VA / (56V x 1.732) = 10.3A
Let's add our fudge factor here to make these numbers a little more
realistic. Once again we will assume a 90% efficiency factor. This
number is only applied to the primary.
2.62A primary x 1.1 = 2.88A corrected primary current.
One important point to remember here is we have calculated the
current for each winding. A 3 phase transformer has 3 input windings
and 3 output windings.
Now we need to calculate the fusing requirements for the transformer.
Electrical Code Article 450-3(b) states that each transformer 600
volts, nominal or less, shall be protected by an individual
overcurrent device on the primary side, rated or set at not more than
125% of the rated primary current of the transformer. Where the
primary current of a transformer is 9 amps or more and 125% of this
current does not correspond to a standard rating of a fuse or
nonadjustable circuit breaker, the next higher standard rating shall
be permitted. Where the primary current is less than 9 amps, an
overcurrent device rated or set at not more than 167% of the primary
current shall be permitted. Where the primary current is less than 2
amps, an overcurrent device rated or set at not more than 300% shall
be permitted.
Electrical Code Article 450-3(b)(2) states if a transformer 600 v,
nominal, or less, having a an overcurrent device on the secondary
side rated or set at not more than 125% of the rated secondary
current of the transformer shall not be required to have an
individual overcurrent device on the primary side if the primary
feeder overcurrent device is rated or set at a current value not more
than 250% of the rated primary current of the transformer.
Electrical Code Article 450-3(b)(2) states that a transformer 600 v,
nominal, or less, shall be protected by an individual overcurrent
device on the secondary side, rated or set at not more than 125% of
the rated secondary current of the transformer. Where the secondary
current of a transformer is 9 amps or more and 125% of this current
does not correspond to a standard rating of a fuse or nonadjustable
circuit breaker, the next higher standard rating shall be permitted.
Where the secondary current is less than 9 amps, an overcurrent
device rated or set at not more than 167% of the secondary current
shall be permitted.
What I get out of these codes is that for our example we have to fuse
the primary and do not have to fuse the secondary. Furthermore our
primary fusing can be as high as 167% of primary current ratting.
For our example 167% of 2.88A = 4.8A fuse maximum per winding. I
would say our minimum fuse size should be 125% to give us a little
safety margin. 125% of 2.88A = 3.6A.
Looking in a Bussman fuse catalog it looks like a FRN-R fuse is
suitable. It is rated for 250V and has moderate inrush capability to
allow the capacitor bank to charge up. The FRN-R has the following
sizes in the range we want. 4A and 4.5A, and once again each leg of
the 3 phase transformer should be fused, for a total of 3 fuses.
Picking the proper fuse for the proper job can be tricky. A 4A fuse
of one style will not behave the same as another style 4A fuse. I
would like to see a good write up on proper fuse selection if anyone
knows of one.
References.
Website were I found 3 phase power calculations and NEC electrical
code info.
http://www.elec-toolbox.com/usefulinfo/xfmr-3ph.htm
Bussman fuse catalog.
http://www.bussmann.com/shared/library/catalogs/FullLine_Cat.pdf
Wally
> cnc_4_me wrote:<john@s...>
>
> >--- In CAD_CAM_EDM_DRO@yahoogroups.com, "John Stevenson"
> >wrote:wound
> >
> >
> >>Transformer shouldn't be a problem as we can get custom ones
> >>were
> >>
> >here with not a lot of problem.
> >
> >
> >>I have a nice one here that outputs 33,000 volts at 5 amps. Is
> >>
> >>
> >California looking for a new electric chair ?
> >
> >165,000 watts or 165Kw. What in the word do you do with it and
> >would you get enough power to use it!!!<john@s...>
> >
> >Our houses in the USA typically have a 220v at 200 amp service.
> >
> >44,000 watts or 44Kw.
> >
> >Wally
> >
> >
> >
> >--- In CAD_CAM_EDM_DRO@yahoogroups.com, "John Stevenson"
> >wrote:is
> >
> >
> >>>Hi John
> >>>
> >>>Just a couple thoughts...
> >>>
> >>>If 20 amps is your maximum peak current per motor you would
> >>>
> >>>
> >certainly
> >
> >
> >>>want to have that capability to prevent nuisance tripping in full
> >>>accel 3-d diagonal moves.
> >>>
> >>>However, depending on the machine, average current requirements
> >>>
> >>>
> >will
> >
> >
> >>>probably
> >>>be much less. In my large low friction router avearage cureent
> >>>or
> >>>
> >less than
> >
> >
> >>>one quarter
> >>>the peak capability.
> >>>
> >>>So I rate the transformer accordingly. The supply capacitor can
> >>>
> >>>
> >deliver the
> >
> >
> >>>full current for short periods just fine...like a fast ramp up
> >>>that
> >>>
> >ramp down.
> >
> >
> >>>I can calculate the cap size requirements but I must know a bit
> >>>
> >>>
> >about the
> >
> >
> >>>machine dynamics.
> >>>
> >>>One other thought I would offer...if individual motors are fused
> >>>
> >>>
> >and only
> >
> >
> >>>one
> >>>fuse blows, the others will perhaps keep going resulting in an
> >>>
> >>>
> >unforseen
> >
> >
> >>>path
> >>>and a possible crash scenario. The estop system must be such
> >>>commonly
> >>>
> >if any one
> >
> >
> >>>axis
> >>>Malfunctions all axes stop. A stop on following error or similar
> >>>
> >>>
> >system can
> >
> >
> >>>do this.
> >>>
> >>>As far as transformers for UK use I am not sure. Custom toroid
> >>>
> >>>
> >kits with a
> >
> >
> >>>pre-wound primary
> >>>and customer wound secondary (about 1 volt per turn) are
> >>>one
> >>>
> >available.
> >
> >
> >>>Les
> >>>
> >>>
> >>>
> >>Les,
> >>This is for a Bridgy Series l conversion using 110volt treadmill
> >>
> >>
> >motors as 100 volt servos.
> >
> >
> >>There will be no 3D moves only two axis will be cutting at any
> >>wound
> >>
> >time, all my work is 2 - 1/2D.
> >
> >
> >>Good point about the fuses, This can be accomplished by power on
> >>
> >>
> >relays wired into the stop circuit.
> >
> >
> >>Transformer shouldn't be a problem as we can get custom ones
> >>wanliker@a..., timg@k...
> >>
> >here with not a lot of problem.
> >
> >
> >>I have a nice one here that outputs 33,000 volts at 5 amps. Is
> >>
> >>
> >California looking for a new electric chair ?
> >
> >
> >>
> >>--
> >>No virus found in this outgoing message.
> >>Checked by AVG Anti-Virus.
> >>Version: 7.0.308 / Virus Database: 266.10.2 - Release Date:
> >>
> >>
> >21/04/2005
> >
> >
> >>
> >>This e-mail was scanned for viruses using BitDefender
> >>
> >>
> >
> >
> >
> >
> >
> >Addresses:
> >FAQ: http://www.ktmarketing.com/faq.html
> >FILES: http://groups.yahoo.com/group/CAD_CAM_EDM_DRO/files/
> >Post Messages: CAD_CAM_EDM_DRO@yahoogroups.com
> >
> >Subscribe: CAD_CAM_EDM_DRO-subscribe@yahoogroups.com
> >Unsubscribe: CAD_CAM_EDM_DRO-unsubscribe@yahoogroups.com
> >List owner: CAD_CAM_EDM_DRO-owner@yahoogroups.com,
> >Moderator: pentam@c... indigo_red@q... davemucha@j...[Moderators]
> >URL to this group: http://groups.yahoo.com/group/CAD_CAM_EDM_DROaol://5863:126/rec.crafts.metalworking or go thru Google.com to reach
> >
> >OFF Topic POSTS: General Machining
> >If you wish to post on unlimited OT subjects goto:
it if you have trouble.
> >http://www.metalworking.com/news_servers.htmlbe a sister site to the CCED group, as many of the same members are
> >
> >http://groups.yahoo.com/group/jobshophomeshop I consider this to
there, for OT subjects, that are not allowed on the CCED list.
> >THEM. DON'T POST IF YOU CAN NOT ACCEPT THIS.....NO EXCEPTIONS........
> >NOTICE: ALL POSTINGS TO THIS GROUP BECOME PUBLIC DOMAIN BY POSTING
> >bill
> >List Mom
> >List Owner
> >
> >
> >Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
>
>
> [Non-text portions of this message have been removed]
Discussion Thread
William Scalione
2000-07-11 19:54:01 UTC
Transformers
John Stevenson
2005-04-24 13:18:18 UTC
Transformers
Leslie Watts
2005-04-24 13:57:28 UTC
RE: [CAD_CAM_EDM_DRO] Transformers
cnc_4_me
2005-04-24 18:56:12 UTC
Re: Transformers
apaulsalerno
2005-04-24 20:31:18 UTC
Re: Transformers
turbulatordude
2005-04-24 22:30:16 UTC
Re: Transformers
Les Newell
2005-04-25 05:31:15 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers
Dave Davies
2005-04-25 06:15:39 UTC
RE: [CAD_CAM_EDM_DRO] Re: Transformers
gary
2005-04-25 06:25:31 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers
Les Newell
2005-04-25 07:36:39 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers
cnc002@a...
2005-04-25 08:13:39 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers
Dave Davies
2005-04-25 09:40:35 UTC
RE: [CAD_CAM_EDM_DRO] Re: Transformers
Alex Holden
2005-04-25 14:02:36 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers
turbulatordude
2005-04-25 14:06:57 UTC
Re: Transformers
turbulatordude
2005-04-25 14:49:03 UTC
Re: Transformers UK source for treadmill motors
Dave Davies
2005-04-25 14:58:01 UTC
RE: [CAD_CAM_EDM_DRO] Re: Transformers
Brian
2005-04-25 15:51:28 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers UK source for treadmill motors
cnc_4_me
2005-04-25 15:58:10 UTC
Re: Transformers 3 phase power calculations and fuse size
Jeff Goldberg
2005-04-25 16:48:55 UTC
RE: [CAD_CAM_EDM_DRO] Re: Transformers 3 phase power calculations and fuse size
Jeff Goldberg
2005-04-25 16:53:17 UTC
RE: [CAD_CAM_EDM_DRO] Re: Re: Transformers 3 phase power calculations and fuse size
Bot Great
2005-04-25 17:58:53 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers UK source for treadmill motors
Pd62448@c...
2005-04-25 17:59:40 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers 3 phase power calculations and fuse size
apaulsalerno
2005-04-25 19:01:24 UTC
Re: Transformers
apaulsalerno
2005-04-25 19:05:09 UTC
Re: Transformers
turbulatordude
2005-04-25 19:14:45 UTC
Re: Transformers
cnc_4_me
2005-04-25 20:29:25 UTC
Re: Transformers 3 phase power calculations and fuse size
apaulsalerno
2005-04-25 22:20:56 UTC
Re: Transformers
Roy J. Tellason
2005-04-26 07:27:20 UTC
Re: [CAD_CAM_EDM_DRO] Re: Re: Transformers 3 phase power calculations and fuse size
Roy J. Tellason
2005-04-26 07:30:20 UTC
Re: [CAD_CAM_EDM_DRO] Re: Transformers 3 phase power calculations and fuse size
Tom
2005-04-26 10:32:45 UTC
Re: [CAD_CAM_EDM_DRO] Re: RE: Re: Re: Transformers 3 phase power calculations and fuse size
David Speck
2005-04-26 19:18:03 UTC
Potential relays