> The electric diagram should show Line 1, 110 volts Line 2, 110 volts
> and a white neutral, I am confused it is indicated L, N, and PE and
> that last PE looked it is grounded to the chassis of the electrical
> box, and more there is a jumper between N and PE,on the other side of
> the connecting bar,in line with N and PE, I am lost The motor is 2hp
> single Phase 220 volts.Can someone help me please.

PE must be protective earth = safety ground. It should be connected to
the 120 V neutral ONLY at the circuit breaker box, not in the equipment,
unless you won't be running a separate wire to the unit. That would be
a violation of the national electrical code.

If this is truly a 220 V motor, and there are no other 120 V loads in
the equipment, then there should be no neutral wire. Just 2 lines
and a safety ground.

Jon

Discussion Thread

pelevesq 2002-06-24 18:30:01 UTC Connecting Motor 220 volts Jon Elson 2002-06-24 22:35:51 UTC Re: [CAD_CAM_EDM_DRO] Connecting Motor 220 volts studleylee 2002-06-25 11:13:14 UTC Re: Connecting Motor 220 volts pelevesq 2002-06-27 18:17:58 UTC Re: Connecting Motor 220 volts