RE: [CAD_CAM_EDM_DRO] Wire size question...
Posted by
Jeff Goldberg
on 2005-04-07 04:07:42 UTC
Jan,
Believe me, this is not meant as a criticism (you know more electronics in
your little finger than I'll ever learn), but an observation based on a
background of being a master electrician. Unless there is some unique
characteristic of a power supply that I'm not taking into account:
The National Electric Code (which is ultra-conservative because it is
written by the Insurance Underwriters) and the NYC Electric Code (written by
people who make the insurance underwriters look liberal) say that #10 wire
size is suitable for carrying 30 amperes 100% duty cycle when installed in
conduit within walls (where the heat created will be retained).
Why would you feel hesitant about using it on a free air application (which
normally allows you to drop to a smaller wire size (think extension cord
wire gauge vs. house wiring wire gauge - not many people use a #12 awg
extension cord for a portable tool which draws 15 amps). Especially on a
short piece (30cm), the #10 awg is technically overkill, but shouldn't be a
problem. Going to #8 awg, my mean changing lugs, and other stuff for no
particular benefit that I can see.
If I've got this wrong, I'm always willing to learn.
Jeff
-----Original Message-----
From: JanRwl@... [mailto:JanRwl@...]
Sent: Wednesday, April 06, 2005 11:59 PM
To: CAD_CAM_EDM_DRO@yahoogroups.com
Subject: Re: [CAD_CAM_EDM_DRO] Wire size question...
In a message dated 4/6/2005 7:57:39 P.M. Central Daylight Time,
loudcouture2003@... writes:
I am building my power supply and i have a simple question, what size (AWG)
of wire should i use for 30 amps for about 30cm?<< If you mean "lead wires"
from the PS to the load, then #8 is about right.
If the load is "30 A. max., intermittent", #10 might do for such a short
run.
Lotsa luck! Jan Rowland
[Non-text portions of this message have been removed]
Addresses:
FAQ: http://www.ktmarketing.com/faq.html
FILES: http://groups.yahoo.com/group/CAD_CAM_EDM_DRO/files/
Post Messages: CAD_CAM_EDM_DRO@yahoogroups.com
Subscribe: CAD_CAM_EDM_DRO-subscribe@yahoogroups.com
Unsubscribe: CAD_CAM_EDM_DRO-unsubscribe@yahoogroups.com
List owner: CAD_CAM_EDM_DRO-owner@yahoogroups.com, wanliker@...,
timg@...
Moderator: pentam@... indigo_red@... davemucha@...
[Moderators]
URL to this group: http://groups.yahoo.com/group/CAD_CAM_EDM_DRO
OFF Topic POSTS: General Machining
If you wish to post on unlimited OT subjects goto:
aol://5863:126/rec.crafts.metalworking or go thru Google.com to reach it if
you have trouble.
http://www.metalworking.com/news_servers.html
http://groups.yahoo.com/group/jobshophomeshop I consider this to be a
sister site to the CCED group, as many of the same members are there, for OT
subjects, that are not allowed on the CCED list.
NOTICE: ALL POSTINGS TO THIS GROUP BECOME PUBLIC DOMAIN BY POSTING THEM.
DON'T POST IF YOU CAN NOT ACCEPT THIS.....NO EXCEPTIONS........
bill
List Mom
List Owner
Yahoo! Groups Links
Believe me, this is not meant as a criticism (you know more electronics in
your little finger than I'll ever learn), but an observation based on a
background of being a master electrician. Unless there is some unique
characteristic of a power supply that I'm not taking into account:
The National Electric Code (which is ultra-conservative because it is
written by the Insurance Underwriters) and the NYC Electric Code (written by
people who make the insurance underwriters look liberal) say that #10 wire
size is suitable for carrying 30 amperes 100% duty cycle when installed in
conduit within walls (where the heat created will be retained).
Why would you feel hesitant about using it on a free air application (which
normally allows you to drop to a smaller wire size (think extension cord
wire gauge vs. house wiring wire gauge - not many people use a #12 awg
extension cord for a portable tool which draws 15 amps). Especially on a
short piece (30cm), the #10 awg is technically overkill, but shouldn't be a
problem. Going to #8 awg, my mean changing lugs, and other stuff for no
particular benefit that I can see.
If I've got this wrong, I'm always willing to learn.
Jeff
-----Original Message-----
From: JanRwl@... [mailto:JanRwl@...]
Sent: Wednesday, April 06, 2005 11:59 PM
To: CAD_CAM_EDM_DRO@yahoogroups.com
Subject: Re: [CAD_CAM_EDM_DRO] Wire size question...
In a message dated 4/6/2005 7:57:39 P.M. Central Daylight Time,
loudcouture2003@... writes:
I am building my power supply and i have a simple question, what size (AWG)
of wire should i use for 30 amps for about 30cm?<< If you mean "lead wires"
from the PS to the load, then #8 is about right.
If the load is "30 A. max., intermittent", #10 might do for such a short
run.
Lotsa luck! Jan Rowland
[Non-text portions of this message have been removed]
Addresses:
FAQ: http://www.ktmarketing.com/faq.html
FILES: http://groups.yahoo.com/group/CAD_CAM_EDM_DRO/files/
Post Messages: CAD_CAM_EDM_DRO@yahoogroups.com
Subscribe: CAD_CAM_EDM_DRO-subscribe@yahoogroups.com
Unsubscribe: CAD_CAM_EDM_DRO-unsubscribe@yahoogroups.com
List owner: CAD_CAM_EDM_DRO-owner@yahoogroups.com, wanliker@...,
timg@...
Moderator: pentam@... indigo_red@... davemucha@...
[Moderators]
URL to this group: http://groups.yahoo.com/group/CAD_CAM_EDM_DRO
OFF Topic POSTS: General Machining
If you wish to post on unlimited OT subjects goto:
aol://5863:126/rec.crafts.metalworking or go thru Google.com to reach it if
you have trouble.
http://www.metalworking.com/news_servers.html
http://groups.yahoo.com/group/jobshophomeshop I consider this to be a
sister site to the CCED group, as many of the same members are there, for OT
subjects, that are not allowed on the CCED list.
NOTICE: ALL POSTINGS TO THIS GROUP BECOME PUBLIC DOMAIN BY POSTING THEM.
DON'T POST IF YOU CAN NOT ACCEPT THIS.....NO EXCEPTIONS........
bill
List Mom
List Owner
Yahoo! Groups Links
Discussion Thread
loudcouture2003
2005-04-06 17:54:50 UTC
Wire size question...
Jeff Goldberg
2005-04-06 18:26:11 UTC
RE: [CAD_CAM_EDM_DRO] Wire size question...
turbulatordude
2005-04-06 18:52:03 UTC
Re: Wire size question...
John Rouche
2005-04-06 19:57:12 UTC
Re: Wire size question...
Jeff Goldberg
2005-04-06 20:17:31 UTC
RE: [CAD_CAM_EDM_DRO] Re: Wire size question...
Jeff Goldberg
2005-04-06 20:20:12 UTC
RE: [CAD_CAM_EDM_DRO] Re: Wire size question...
JanRwl@A...
2005-04-06 20:59:20 UTC
Re: [CAD_CAM_EDM_DRO] Wire size question...
loudcouture2003
2005-04-07 00:46:48 UTC
Re: Wire size question...
Jeff Goldberg
2005-04-07 04:07:42 UTC
RE: [CAD_CAM_EDM_DRO] Wire size question...
John Rouche
2005-04-07 06:30:20 UTC
Re: Wire size question...
Roy J. Tellason
2005-04-07 08:59:31 UTC
Re: [CAD_CAM_EDM_DRO] Re: Wire size question...
JanRwl@A...
2005-04-07 14:05:30 UTC
Re: [CAD_CAM_EDM_DRO] Wire size question...