CAD CAM EDM DRO - Yahoo Group Archive

Re: The 250 byte packet viz. ESTOP

Posted by ptkeillor3
on 2006-05-21 07:42:04 UTC
--- In CAD_CAM_EDM_DRO@yahoogroups.com, Wayne Weedon <wayne@...>
wrote:
>
> John Dammeyer wrote:
>
> >Hi Mark,
> >
> >If the USB dongle is receiving 250 bytes every 10mS and checks
the ESTOP and
> >limit switches every 40uS then even if there wasn't a immediate
message to
> >the PC via USB to tell it that an ESTOP occurred worst case would
still be
> >only 10mS.
> >
> >
> E-stop signal to the cpu should only be a signal to say E-stop has
> occured. Normally E-stops are hard wired externally, and any
processor
> will have nothing to do with it.
>
> Drive(s) shutdown is all handled by the estop relay on all my
retrofits,
> but then at least here in the UK it's a legal requirement to do it
this
> way. I'd expect it's much the same elsewhere.
>
<snip sig>

I handle E-stops similarly, although in an unrelated field (chemical
processing). First, I'm just a lurker here, interested in someday
building a hobby router. On my lab rigs (automated chemical
processing miniplants), I generally use a main power relay, with all
E-stop activity controlling the relay. Opening the main relay
usually stops all pumps, motors, and heaters, but not always. It
depends on the process.

Things that need to be are hardwired in series (usually E-stop
buttons) and one relay in the series is controlled by the control
program. This is because the control station is or can be remote,
and other conditions (usually temp and pressure) may require an E-
stop. The power to the 24VDC power supply comes off ahead of the
main relay because in this situation I need to know what's going on
in the process. Chemical processes don't necessarily stop if you
cut power.

In any case, I try to anticipate and test for anything that might
contribute to an unsafe condition, and design accordingly. This
could include dumping or quenching reactants. An extreme and huge
case is light hydrocarbon plants, which must have automatic and
redundant flaring of all products on loss of refrigeration
compressors or product pump power. Otherwise, you have the world's
biggest fuel-air bomb.

At least in the CNC world, when you cut the power everything stops,
so that would be the safest condition.

Regards,

Pete Keillor

Discussion Thread

Mark 2006-05-19 16:37:36 UTC The 250 byte packet viz. ESTOP John Dammeyer 2006-05-19 17:03:37 UTC RE: [CAD_CAM_EDM_DRO] The 250 byte packet viz. ESTOP Wayne Weedon 2006-05-20 04:44:54 UTC Re: [CAD_CAM_EDM_DRO] The 250 byte packet viz. ESTOP John Dammeyer 2006-05-20 09:59:35 UTC RE: [CAD_CAM_EDM_DRO] The 250 byte packet viz. ESTOP delmar williams 2006-05-20 10:36:08 UTC RE: [CAD_CAM_EDM_DRO] The 250 byte packet viz. ESTOP ballendo 2006-05-20 22:21:12 UTC Re: The 250 byte packet viz. ESTOP Wayne Weedon 2006-05-21 03:25:01 UTC Re: [CAD_CAM_EDM_DRO] The 250 byte packet viz. ESTOP ptkeillor3 2006-05-21 07:42:04 UTC Re: The 250 byte packet viz. ESTOP ballendo 2006-05-22 01:50:25 UTC Estop consids was Re: The 250 byte packet viz. ESTOP ptkeillor3 2006-05-22 03:48:17 UTC Estop consids was Re: The 250 byte packet viz. ESTOP