Re: [CAD_CAM_EDM_DRO] Re: VFD single phase 5hp

Posted by David Speck
on 2006-06-21 21:18:58 UTC
Technically, Pete is correct, but be sure that the VFD you buy is spec'd
to run on single phase input. I have some Yaskawa VFDs that have a
missing phase detector, and will shut down of they don't get proper
three phase input on all the input pins. Be sure to check the detailed
specs before you pay for one that won't work for you.

Dave

> Basically it's the input section that needs to be derated when running
> on single phase input. All of the current will be supplied from two
> legs of the rectifier bridge instead of three, and the filter caps will
> see more ripple. Everything from the DC bus on is pretty much
> unaffected.
>
> ~petev
>

Discussion Thread

Callcbm 2006-06-21 18:07:40 UTC VFD single phase 5hp vavaroutsos 2006-06-21 19:29:16 UTC Re: VFD single phase 5hp paultitchener 2006-06-21 20:55:59 UTC Re: VFD single phase 5hp Jon Elson 2006-06-21 20:58:47 UTC Re: [CAD_CAM_EDM_DRO] VFD single phase 5hp David Speck 2006-06-21 21:18:58 UTC Re: [CAD_CAM_EDM_DRO] Re: VFD single phase 5hp Jeff Goldberg 2006-06-22 03:30:05 UTC [CAD_CAM_EDM_DRO] VFD single phase 5hp turbulatordude 2006-06-22 04:49:18 UTC Re: VFD single phase 5hp Al Daniel 2006-06-22 08:14:17 UTC Re: VFD single phase 5hp Jon Elson 2006-06-22 10:15:16 UTC Re: [CAD_CAM_EDM_DRO] Re: VFD single phase 5hp