CAD CAM EDM DRO - Yahoo Group Archive

Re: Transformer Soft Start

Posted by caudlet
on 2003-07-03 17:23:16 UTC
--- In CAD_CAM_EDM_DRO@yahoogroups.com, Bob Simon <bsimon@q...> wrote:
>
> >
>
> Here's what's happening;
>
> When a transformer is switched on, a transient current flows. The
value of
> this current over the first half cycle of mains voltage exceeds the
normal
> magnetizing current by a very large factor, and is often sufficient
to blow
> the primary fuse or lead to excessive tripping of the input circuit
> breaker. This current decays exponentially over several cycles
until normal
> magnetizing current flows.
>
> This phenom is common in machine tool and welding transformers,
even with
> no load on the secondaries. ie; Even though the panel on the
machine says
> 50FLA, a 100A circuit breaker feeding the machine trips out when
the
> cabinet switch on the machine is thrown.
>
> Standard breakers and fuses react too fast to the inrush current.
What's
> needed is a slower disconnect to allow the current to settle to
normal levels.
>
> We usually install a high inrush delay circuit breaker that can
handle a 3X
> overcurrent for a couple of cycles. No more problem trips. Dual
element

Bob, You are totally right. The amount of inrush current to a
transformer is a factor of the magnetization curve of the core and
the angle (sin) of the voltage wave at turnon. Problems occur
because the inrush voltage at an improper phase angle causes the
magnetic core of the transformer to saturate and draw many times the
normal current. A large inductor like the power transformer shows
peak current when it is switched on at the zero crossing point of the
AC waveform. This is exactly opposite of a resistive or capacitive
load which operates best at zero crossing. If the transformer is
switched on at peak (and there is no residual core magnetization)
then the inrush current is minimal.

I have seen a scheme (EDN I think) where a slave relay circuit is
used to limit inrush current. They put a resistor in series with one
of the AC transformer legs and a NO relay's contacts in parallel.
The small DC supply for the relay coil (derived from the ac line) has
an RC factor that causes it to delay turning on and shorting out the
resistor for a few cycles. While it is more complex than using a
thermistor it has the advantage of being a low loss device and it
will operate without regard to a cool-down cycle required by the
thermistor device.

Delay fuses will work but the stress of magnetic saturation on the
other components can take its toll.

Discussion Thread

tiffyted 2003-07-03 02:25:45 UTC Transformer Soft Start Les Newell 2003-07-03 05:35:57 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start rainnea 2003-07-03 06:54:12 UTC Re: Transformer Soft Start Tim Goldstein 2003-07-03 08:01:56 UTC RE: [CAD_CAM_EDM_DRO] Transformer Soft Start Les Newell 2003-07-03 08:23:13 UTC Re: [CAD_CAM_EDM_DRO] Re: Transformer Soft Start Jon Elson 2003-07-03 08:43:24 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Carl Mikkelsen 2003-07-03 09:37:19 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Tony Jeffree 2003-07-03 10:11:03 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Ted Walls 2003-07-03 10:28:14 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Tim Goldstein 2003-07-03 10:36:48 UTC RE: [CAD_CAM_EDM_DRO] Transformer Soft Start wanliker@a... 2003-07-03 10:57:05 UTC Transformer Soft Start Keith Bowers 2003-07-03 11:22:13 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start caudlet 2003-07-03 12:51:15 UTC Re: Transformer Soft Start rainnea 2003-07-03 13:30:39 UTC Re: Transformer Soft Start Les Newell 2003-07-03 14:03:03 UTC Re: [CAD_CAM_EDM_DRO] Re: Transformer Soft Start Paul 2003-07-03 14:38:13 UTC Re: [CAD_CAM_EDM_DRO] Re: Transformer Soft Start Bob Simon 2003-07-03 14:44:23 UTC Re: [CAD_CAM_EDM_DRO] Re: Transformer Soft Start caudlet 2003-07-03 17:23:16 UTC Re: Transformer Soft Start Jon Elson 2003-07-03 21:43:02 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Jon Elson 2003-07-03 21:52:19 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Graham Stabler 2003-07-04 03:31:28 UTC Re: Transformer Soft Start