Re: [CAD_CAM_EDM_DRO] Transformer Soft Start

Posted by Jon Elson
on 2003-07-03 21:52:19 UTC
Ted Walls wrote:

>tiffyted wrote:
>
>
>
>>Can anyone in this group advise me on a suitable circuit for soft
>>starting a 230v primary, 40v secondary 1000VA toriordal transformer.
>>
>>
>
>Jon Elson Replied:
>
> I think you have something serious wrong, here. I don't think soft start
>will help you.....
>
>Thanks for the reply Jon,
>
>The transformer is 230v only primary and 2 x 40v 12.5A secondary. As
>supplied by RS. It currently is not connected to any rectification circuit
>and the secondary windings are open circuit.
>
>I have checked the data sheet which indicates the normal running current
>would be 4.34A. However, there is a paragraph that states the start current
>can momentarily be as much as 67 times this, which would blow the fuse. This
>is what led me to assume I needed a soft start system.
>
>
The problem with transformers is that they are designed to use minimum
materials.
So, the core is just enough to handle the normal integration of voltage
* time, which
always balances out to zero over a full cycle. but, if the transformer
is turned on
at about zero volts, it is starting out with no magnetic field, and has
to integrate the
full half-cycle of one polarity without previously been fully charged
with the reverse
polarity from the previous half cycle. This causes the iron in the
transformer to
saturate, and the normal inductance of the transformer disappears,
leaving only the
wire resistance to limit current. This is why some power supplies produce a
loud hum when first turned on.

The surge limiter (Negative Temp Coefficient) devices are about one US
Dollar
each. You will need one of the big ones for this application. But, I'm
not sure
it will solve the problem. The saturated iron should resolve itself
after a half cycle
of the transformer. 67 x nominal load for one half cycle is not an extreme
event for motors and rectifier power supplies. You should really try
the light
bulb limiter first to make sure it is not a bad transformer (or the wrong
transformer, wrong wiring, etc.) Hmm, is there any possibility you have the
mains connected to the secondary?

Jon

>Les Newell has suggested that I use a surge arrester. I think if they are
>not too pricey I'll get one to try. If it works Ok I'll let you all know. If
>not I'll have to look into it a bit deeper.
>
>Thanks again to all for their replies.
>
>
>
>
>Addresses:
>FAQ: http://www.ktmarketing.com/faq.html
>FILES: http://groups.yahoo.com/group/CAD_CAM_EDM_DRO/files/
>Post Messages: CAD_CAM_EDM_DRO@yahoogroups.com
>
>Subscribe: CAD_CAM_EDM_DRO-subscribe@yahoogroups.com
>Unsubscribe: CAD_CAM_EDM_DRO-unsubscribe@yahoogroups.com
>List owner: CAD_CAM_EDM_DRO-owner@yahoogroups.com, wanliker@..., timg@...
>Moderator: pentam@... indigo_red@... [Moderators]
>URL to this group: http://groups.yahoo.com/group/CAD_CAM_EDM_DRO
>
>OFF Topic POSTS: General Machining
>If you wish to post on unlimited OT subjects goto: aol://5863:126/rec.crafts.metalworking or go thru Google.com to reach it if you have trouble.
>http://www.metalworking.com/news_servers.html
>
>http://groups.yahoo.com/group/jobshophomeshop I consider this to be a sister site to the CCED group, as many of the same members are there, for OT subjects, that are not allowed on the CCED list.
>
>NOTICE: ALL POSTINGS TO THIS GROUP BECOME PUBLIC DOMAIN BY POSTING THEM. DON'T POST IF YOU CAN NOT ACCEPT THIS.....NO EXCEPTIONS........
>bill
>List Mom
>List Owner
>
>
>
>Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
>
>
>
>

Discussion Thread

tiffyted 2003-07-03 02:25:45 UTC Transformer Soft Start Les Newell 2003-07-03 05:35:57 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start rainnea 2003-07-03 06:54:12 UTC Re: Transformer Soft Start Tim Goldstein 2003-07-03 08:01:56 UTC RE: [CAD_CAM_EDM_DRO] Transformer Soft Start Les Newell 2003-07-03 08:23:13 UTC Re: [CAD_CAM_EDM_DRO] Re: Transformer Soft Start Jon Elson 2003-07-03 08:43:24 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Carl Mikkelsen 2003-07-03 09:37:19 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Tony Jeffree 2003-07-03 10:11:03 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Ted Walls 2003-07-03 10:28:14 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Tim Goldstein 2003-07-03 10:36:48 UTC RE: [CAD_CAM_EDM_DRO] Transformer Soft Start wanliker@a... 2003-07-03 10:57:05 UTC Transformer Soft Start Keith Bowers 2003-07-03 11:22:13 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start caudlet 2003-07-03 12:51:15 UTC Re: Transformer Soft Start rainnea 2003-07-03 13:30:39 UTC Re: Transformer Soft Start Les Newell 2003-07-03 14:03:03 UTC Re: [CAD_CAM_EDM_DRO] Re: Transformer Soft Start Paul 2003-07-03 14:38:13 UTC Re: [CAD_CAM_EDM_DRO] Re: Transformer Soft Start Bob Simon 2003-07-03 14:44:23 UTC Re: [CAD_CAM_EDM_DRO] Re: Transformer Soft Start caudlet 2003-07-03 17:23:16 UTC Re: Transformer Soft Start Jon Elson 2003-07-03 21:43:02 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Jon Elson 2003-07-03 21:52:19 UTC Re: [CAD_CAM_EDM_DRO] Transformer Soft Start Graham Stabler 2003-07-04 03:31:28 UTC Re: Transformer Soft Start