RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Posted by
Jeff Goldberg
on 2003-02-13 13:07:55 UTC
Thanks for the input. The NC controller has a bunch of large ceramic
resistors in the bottom of the enclosure. The three axis circuit boards
(labeled drive, so I guess that's what they are) are loaded with power
transistors and smaller ceramic resistors if this helps with the
identification of the type controller I have.
If I understand you, the controller resisters are in series with the motor
resistors and create a voltage divider?
I measured the winding resistance (by wiring the four stepper coils in
series, measuring, and dividing by four) and the per winding resistance
comes to .3 ohm.
I plugged the cables from the resistors in the controller into the axis
drive board (in case my readings would be modified by some of the stuff on
the board). Measuring across each of the four resistors I get 2.2, 2.2, 2.7
and 2.7 ohms respectively.
This is being fed by 130 volts A.C.
I'm clueless about how the four controller resistors are combined to create
the final resistance to use with the motor resistance to find out what the
original motor voltage was.
Any help would be greatly appreciated.
Thanks and regards,
Jeff
-----Original Message-----
From: Tony Jeffree [mailto:tony@...]
Sent: Thursday, February 13, 2003 11:55 AM
To: CAD_CAM_EDM_DRO@yahoogroups.com
Subject: RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON
STEPPER MOTORS - ref post 52721
Jeff -
An interesting problem - without knowledge of the motor's current rating,
it is a little difficult to advise on a current setting for the controller
cards.
From your earlier posts, it sounds like the original drives may well have
been simple L/R drives (using power resistors in series with the motor
coils to limit the current). If this is so, then you should be able to work
back to the motor current rating; divide the supply voltage by the ratio of
the motor coil resistance to the series power resistor value to get the
voltage needed to drive the max current. From I=R/E you can then work out
what current that voltage will drive through the motor coil
resistance. However, to do this successfully, you would need to know what
the drive circuitry really is - whether it is a "simple" L/R drive, or a
more sophisticated drive (a bi-level chopper, for example). If the latter,
then it may not be so easy to determine by this method.
An alternative "empirical" method might be to hook one motor up to a drive,
and adjust the current up until the motor gets warm (giving enough time
between current increments for the motor temperature to stabilize).
Steppers are generally designed to run warm; if you set the current such
that the motor gets warm (but not too hot to touch) you probably are not
far off the right current setting.
Regards,
Tony
At 11:04 13/02/2003 -0500, you wrote:
resistors in the bottom of the enclosure. The three axis circuit boards
(labeled drive, so I guess that's what they are) are loaded with power
transistors and smaller ceramic resistors if this helps with the
identification of the type controller I have.
If I understand you, the controller resisters are in series with the motor
resistors and create a voltage divider?
I measured the winding resistance (by wiring the four stepper coils in
series, measuring, and dividing by four) and the per winding resistance
comes to .3 ohm.
I plugged the cables from the resistors in the controller into the axis
drive board (in case my readings would be modified by some of the stuff on
the board). Measuring across each of the four resistors I get 2.2, 2.2, 2.7
and 2.7 ohms respectively.
This is being fed by 130 volts A.C.
I'm clueless about how the four controller resistors are combined to create
the final resistance to use with the motor resistance to find out what the
original motor voltage was.
Any help would be greatly appreciated.
Thanks and regards,
Jeff
-----Original Message-----
From: Tony Jeffree [mailto:tony@...]
Sent: Thursday, February 13, 2003 11:55 AM
To: CAD_CAM_EDM_DRO@yahoogroups.com
Subject: RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON
STEPPER MOTORS - ref post 52721
Jeff -
An interesting problem - without knowledge of the motor's current rating,
it is a little difficult to advise on a current setting for the controller
cards.
From your earlier posts, it sounds like the original drives may well have
been simple L/R drives (using power resistors in series with the motor
coils to limit the current). If this is so, then you should be able to work
back to the motor current rating; divide the supply voltage by the ratio of
the motor coil resistance to the series power resistor value to get the
voltage needed to drive the max current. From I=R/E you can then work out
what current that voltage will drive through the motor coil
resistance. However, to do this successfully, you would need to know what
the drive circuitry really is - whether it is a "simple" L/R drive, or a
more sophisticated drive (a bi-level chopper, for example). If the latter,
then it may not be so easy to determine by this method.
An alternative "empirical" method might be to hook one motor up to a drive,
and adjust the current up until the motor gets warm (giving enough time
between current increments for the motor temperature to stabilize).
Steppers are generally designed to run warm; if you set the current such
that the motor gets warm (but not too hot to touch) you probably are not
far off the right current setting.
Regards,
Tony
At 11:04 13/02/2003 -0500, you wrote:
>Guys:
>
>I really appreciate the input. I'm a newbie at this and your
>discussion is very helpful. As a follow on question:
>
>I have the following challenges:
>The DC power supply of the NC controller I'm cannibalizing puts out
>130V. I don't know if this eventually reached the motors or was
>reduced somewhere else in the old NC drive section before reaching the
>drives. (There was a short circuit somewhere in the unit, so I
>disconnected all the controls, drives etc so I could work on the power
>supply). I can rewire the taps on the transformer to give me either 62
>or 68 volts DC, both of which fall below the range of the 80v max of
>the CMD260 drives I bought.
>
>Based on the input you guys gave (my NEMA 42 steppers are unmarked and
>undocumented) I'm going to try running them in parallel. I really
>don't want to generate sparks and a puff of smoke. What would you
>recommend the current setting on the drives to be placed at (they go as
>high as 8 amps)? Should I drive them with 62 volts or 68 volts?
>
>Thanks in advance,
>
>Jeff
>
>
>-----Original Message-----
>From: turbulatordude <davemucha@...> [mailto:davemucha@...]
>Sent: Thursday, February 13, 2003 8:33 AM
>To: CAD_CAM_EDM_DRO@yahoogroups.com
>Subject: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON
>STEPPER MOTORS - ref post 52721
>
>
>
>The serial vs. parallel speed question was tossed around by the pros
>from Dover a little while back.
>
>This is real close of an explanation. if you want more, read the whole
>thread.
>
>
>Message 52721 "jeffalanp" <xylotex@h. . . > Date: Tue Nov 19, 2002
>12:56 am Subject: Re: Running Unipolar steppers with a Bi-polar driver?
>
>"Mariss, OK, OK, I got it (I think). The inductive time constant for
>both parallel and series motors will be the same (t=L/R, the time it
>take to get to 62. 3%). But to overcome the increased inductance and
>resistance in a series wound motor (compared to parallel), I would need
>to double the voltage to achieve the same time as parallel. "
>
>There was more on the post, time to charge the coil, discharge it, then
>reverse direction, that sort of stuff. but this is enough data for
>most of us to understand the differences.
>
>Or the short and sweet, series goes thru a longer wire and that takes
>more time. You can did deeper and get more data.
>
>Dave
>
>
>
>
>
>--- In CAD_CAM_EDM_DRO@yahoogroups.com, Alper YILDIRIM
><yildirimalper@y...> wrote:
> > Hi,
> > Take a look to the following site:
> >
> > http://www.microkinetics.com/contab.html
> >
> > For the bipolar series and parallel connections the
> > time constant L/R is same. For parallel connection, inductance lower
> > 4 times but resistance lowers 4 times too. So the time sonstant does
> > not change. Can someone explain why parallel wiring allows higher
> > speeds according to this approach.
> >
> > Best regards
> > Alper
> >
> > Jon wrote:
> >
> > ""Yes. In almost all cases, the parallel connection
> > is better. It
> > provides lower inductance,
> > and therefore, higher speeds, than the series
> > connection. The only
> > time
> > to use series
> > is if your stepper driver cannot supply the current
> > needed for parallel
> > connection, and
> > if high speed is not important. (The fix is to get a driver that
> > CAN handle full rated
> > current in the parallel mode.)
> > Jon""
> >
> >
> > __________________________________________________
>
>
>
Discussion Thread
washcomp <jeff@w...
2003-02-12 06:25:30 UTC
QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS
Jon Elson
2003-02-12 10:09:46 UTC
Re: [CAD_CAM_EDM_DRO] QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS
Alper YILDIRIM
2003-02-13 02:44:07 UTC
Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS
turbulatordude <davemucha@j...
2003-02-13 05:33:19 UTC
Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Nigel Bailey
2003-02-13 06:54:06 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-13 08:04:19 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Tony Jeffree
2003-02-13 08:53:29 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jon Elson
2003-02-13 09:28:41 UTC
Re: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS
Mariss Freimanis <mariss92705@y...
2003-02-13 10:06:34 UTC
Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-13 13:07:55 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Tony Jeffree
2003-02-13 14:19:55 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-13 15:56:36 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
turbulatordude <davemucha@j...
2003-02-13 17:35:52 UTC
Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-13 19:27:53 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
turbulatordude <davemucha@j...
2003-02-13 20:57:42 UTC
Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jon Elson
2003-02-13 21:30:23 UTC
Re: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jon Elson
2003-02-13 21:43:58 UTC
Re: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Tony Jeffree
2003-02-13 22:18:34 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Mariss Freimanis <mariss92705@y...
2003-02-13 22:25:44 UTC
Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
turbulatordude <davemucha@j...
2003-02-14 05:13:31 UTC
Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Nigel Bailey
2003-02-14 07:39:08 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jon Elson
2003-02-14 09:26:27 UTC
Re: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-14 14:07:55 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-15 12:23:27 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Tim Goldstein
2003-02-15 12:32:21 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-15 13:10:18 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-15 14:26:10 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jeff Goldberg
2003-02-16 07:48:25 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Tim Goldstein
2003-02-16 08:40:44 UTC
RE: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721
Jon Elson
2003-02-16 15:11:47 UTC
Re: [CAD_CAM_EDM_DRO] Re: QUESTION ABOUT SERIES OR PARALLEL ON STEPPER MOTORS - ref post 52721