CAD CAM EDM DRO - Yahoo Group Archive

Re: ELCB Issues

Posted by xj5373
on 2007-03-18 13:31:59 UTC
Thanks for this.

I guess the thing that bothers me is that once the machine is up and
running, like this morning for example, everything works normally and
the trip stays in. So it seems that in normal circumstances there is
no imbalance between live and neutral, it seems to be something that
happens just when the charge pump relay powers up the inverter and
the stepper power supply, hence my suggestion of some kind of
transient.

Once powered up the Inverter (spindle) can be switched on and off
with no ill effects, the steppers similarly work without problems.

Ian

--- In CAD_CAM_EDM_DRO@yahoogroups.com, "Mark Vaughan" <mark@...>
wrote:
>
> Hi Lester and Ian
>
> As Lester say the cause is an Earth fault, but it is easy to get
some
> confusion here, so first you must consider how the ELCB works.
>
> It does not detect current in the Earth wire, it looks at the live
and
> neutral, the current travelling in each should be the same, if some
is
> leaking to earth then live and neutral will be imbalanced and the
trip will
> go.
>
> So you have to be looking for something, insulation failing
probably between
> Live and Earth, or perhaps a short occurring between Neutral and
Earth.
>
> Like Lester I have found loads of problems with USA kit, and lots
of stuff
> that would never come near their UL safety specs.
>
>
>
> Things to look for.
>
> Failed Suppression capacitors on motors filters and the like. These
will
> often be wired in a Y with a cap between the phases, and one from
each phase
> to earth, a failure here and the ELCB will go. In the UK we use
special
> capacitors that fail short circuit, or open circuit, but others
seem to just
> use a hi voltage cap.
>
>
>
> Insulation in the motor, hopefully it will be a chaffed wire, or
spur on the
> terminals.
>
>
>
> VFD's will dump enormous energy on power up, all you can do for
these is put
> a separate supply in for the machine with an ELCB rated to allow a
higher
> earth current.
>
> Some motors while they have good insulation have enough capacitance
between
> the windings and earth to trip an ELCB, again a high rated ELCB is
required.
>
>
>
> If you use a high rated ELCB (really lower rated in terms of
safety), only
> use it as a supply for the machine, and only do this if you are
sure there
> is no fault and have tested the insulation resistance with a proper
> insulation tester, 600V test should be OK though I normally check
at 1KV and
> higher. Remember this supply is no longer as safe, whilst you
wouldn't want
> to do it, you can stick your finger in the mains on most ELCB house
supplies
> ans it will trip before anything nasty happens, you just get a
joult. On my
> mill for the VFD I had to up the trip current to 750mA, this
provides very
> little protection, fingers in there and it will kill, so every
thing is
> double insulated just in case, about the only protection it gives
is to shut
> the supply off if the wires catch on fire.
>
> There are also certain legal issues if you change the ELCB supply
now in the
> UK under Part P of building regs. Many people ignore this, but you
should be
> aware and if in any doubt at all, safety is the issue, the law I
feel is
> second to that, and if you have any doubts seek professional help.
>
>
>
>
>
> Dr. Mark Vaughan Ph'D. B.Eng. M0VAU
>
> Managing Director
>
> Vaughan Industries Ltd, reg in UK no 2561068
>
> Water Care Technology Ltd, reg in UK no 4129351
>
> Addr Unit3, Sydney House, Blackwater, Truro, Cornwall, TR4 8HH, UK.
> Phone/Fax 44 1872 561288
>
> _____
>
> From: CAD_CAM_EDM_DRO@yahoogroups.com
> [mailto:CAD_CAM_EDM_DRO@yahoogroups.com] On Behalf Of Lester Caine
> Sent: 18 March 2007 08:34
> To: CAD_CAM_EDM_DRO@yahoogroups.com
> Subject: Re: [CAD_CAM_EDM_DRO] ELCB Issues
>
>
>
> xj5373 wrote:
> > Hi,
> > I have stripped out the old control system from a Denford
Easimill and
> > replaced with Mach3 via a Bob Campbell break out board. It works
> > beautifully but from the start I had a problem with the machine
> > dropping out the ELCB on the mains supply. The machine is plugged
into
> > a ring main which is fed via an earth leakage circuit breaker
from our
> > consumer unit (I should say that I am in the UK). I found that if
I
> > Estopped Mach3, this drops a relay connected to the change pump
which
> > takes the power off the stepper power supply. Giving it a minute
or two
> > allowed me to isolate the machine from the mains without the ELCB
> > dropping.....more often than not. Isolating immedaitely after
Estop
> > seemed more likely to drop the ELCB. I have opeated this way
since last
> > summer but just now I can't reset without losing the ELCB. I have
the
> > machine powered up but in Estop mode, pressing reset powers the
relay
> > via the charge pump output of the break out board which switches
240V
> > onto the stepper power supply and the inverter which is
controling
> > spindle speed.
> > I know what the ELCB does but what is it that is tripping it? Any
help
> > or hints greatly appreciated.
>
> The only thing that will trip the ELCB is an earth fault. So there
must be
> something giving feedback into the protective earth. The first
thing I would
>
> be looking at is what is connected to that earth. I don't like the
mains
> arrangements on any of the American boards I've seen and none of
them pass
> the
> European creepage and clearance rules. Which need to be need to be
a good 2
> times that needed for 110V ;) So I tend to stick to external mains
> components
> such as solid state relays and just run DC from the boards. Then
you can
> ensure clean live and neutral connections.
>
> --
> Lester Caine - G8HFL
> -----------------------------
> Contact - http://home. <http://home.lsces.co.uk/lsces/wiki/?
page=contact>
> lsces.co.uk/lsces/wiki/?page=contact
> L.S.Caine Electronic Services - http://home.
<http://home.lsces.co.uk>
> lsces.co.uk
> MEDW - http://home.
<http://home.lsces.co.uk/ModelEngineersDigitalWorkshop/>
> lsces.co.uk/ModelEngineersDigitalWorkshop/
> Treasurer - Firebird Foundation Inc. - http://www.firebird
> <http://www.firebirdsql.org/index.php> sql.org/index.php
>
>
>
>
>
> [Non-text portions of this message have been removed]
>

Discussion Thread

xj5373 2007-03-18 01:09:13 UTC ELCB Issues Lester Caine 2007-03-18 01:33:30 UTC Re: [CAD_CAM_EDM_DRO] ELCB Issues xj5373 2007-03-18 06:00:17 UTC Re: ELCB Issues Lester Caine 2007-03-18 08:24:15 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues Kevin Martin 2007-03-18 09:17:53 UTC RE: [CAD_CAM_EDM_DRO] Re: ELCB Issues Wayne Weedon 2007-03-18 11:25:39 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues xj5373 2007-03-18 12:50:51 UTC Re: ELCB Issues Mark Vaughan 2007-03-18 13:09:21 UTC RE: [CAD_CAM_EDM_DRO] ELCB Issues xj5373 2007-03-18 13:31:59 UTC Re: ELCB Issues Lester Caine 2007-03-18 13:50:10 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues Mark Vaughan 2007-03-18 13:55:14 UTC RE: [CAD_CAM_EDM_DRO] Re: ELCB Issues Mark Vaughan 2007-03-18 14:01:30 UTC RE: [CAD_CAM_EDM_DRO] Re: ELCB Issues Wayne Weedon 2007-03-18 14:17:53 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues Mark Vaughan 2007-03-18 14:26:01 UTC RE: [CAD_CAM_EDM_DRO] Re: ELCB Issues Jon Elson 2007-03-18 18:09:24 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues Steve Blackmore 2007-03-18 18:27:06 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues Harko Schwartz 2007-03-18 20:57:26 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues Lester Caine 2007-03-19 00:09:50 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues Mark Vaughan 2007-03-19 01:07:10 UTC RE: [CAD_CAM_EDM_DRO] Re: ELCB Issues Mark Vaughan 2007-03-19 01:13:05 UTC RE: [CAD_CAM_EDM_DRO] Re: ELCB Issues Mark Vaughan 2007-03-19 01:20:38 UTC RE: [CAD_CAM_EDM_DRO] Re: ELCB Issues Steve Blackmore 2007-03-19 02:32:55 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues David G. LeVine 2007-03-19 11:23:59 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues Rexarino 2007-03-19 20:37:51 UTC Re: [CAD_CAM_EDM_DRO] Re: ELCB Issues xj5373 2007-04-19 11:38:53 UTC Re: ELCB Issues Mark Vaughan 2007-04-19 15:19:58 UTC RE: [CAD_CAM_EDM_DRO] Re: ELCB Issues Luke1027 2007-04-20 11:51:37 UTC [CAD_CAM_EDM_DRO] DC Motors Servo Control Servo System Book --> FREE abdeljalil hasan 2007-04-20 16:37:29 UTC Re: [CAD_CAM_EDM_DRO] DC Motors Servo Control Servo System Book --> FREE Luke1027 2007-04-20 18:48:34 UTC Re: [CAD_CAM_EDM_DRO] DC Motors Servo Control Servo System Book --> FREE