Re: Toroidal transformer ratings?? What after being rectified?

on 2005-01-27 06:45:41 UTC
--- In CAD_CAM_EDM_DRO@yahoogroups.com, Jon Elson <elson@p...> wrote:
> R Rogers wrote:
>
> >Thanks to all who responded. Now, what happens to this amperage
rating after it goes through a rectifier? I know the DC voltage will
increase by a factor of 1.416 due to the RMS. Does the amperage stay
the same or decrease due to the increased voltage?
> >
> >
> This gets REALLY messy, fast. The problem is the rectifier is a
> non-linear component,
> and in this application the transformer is required to deliver
short
> pulses of high
> current as it recharges the capacitor bank only at the voltage peak
of
> the sine wave.
> There are some rough rules of thumb, but they depend strongly on
transformer
> leakage inductance and the ratio of capacitor size to current draw
(or
> the DC ripple
> is another way of expressing it). Power supplies with very low
ripple
> are the worst,
> because the cap is charged for the shortest duration. I've seen
numbers
> varying
> from roughly 50% to 75% of the pure resistive rating for capacitor
input
> filters.
> Sometimes adding a small series resistance (in this case a fraction
of
> an ohm)
> somewhere between the transformer and cap can reduce the current
peaks
> without
> seriously affecting regulation.
>
> Jon


When I first started looking for components, I was thinking 21 amps.
(3 motors, 7 amps each) but after a little contemplation, I realized
how the power moves.

My motors are 1.7 volts, 7 amps. or roughly 12 watts. ( volts times
amps = watts)

at 25x for the power supply, I was hoping for a 42 volts power supply.

working backwards, that is 42 divided by 1.414 or a 29 volt AC
transformer. I had a 24 volt transformer so used that.

I used a pair of the MPJA 10 amp transformers to get 20 amps although
I supposedly will never need more than about 13 amps (66% of full
load for the Geckos)

so... 24 volts times 20 amps = 480 watts after the transformer.
then the loss of about 1.2 volts thru the bridge (23.8 volts) times
1.414 (peak voltage) = 33.6 volts.

480 watts at 24 VAC = 20 amps
480 watts at 33.6 volts = 14.2 amps, Quite a difference.
and, 480 watts at 110VAC = 4.36 amps

So, I needed to size wires according to the amp load at the voltage.

As Jon mentioned, there are peak demands for power at the top of the
AC wave, but I did not considder that as part of my sizing.

In reality, my machine runs one axis at a time so I could actually
size for one motor and scale things back quite a bit. I didn't as
the possibility I will run all three axis at some future time does
exist.

What I am unclear about is the 66% of rating for the power supplies.
using Gecko 201's, and a 7 amp motor, with a nameplate of 1.7 votls,
I theoretically need 12 watts, 24 watts if both phases need to be
included. But, at the higher voltage, the supplied wattage is HUGE
compared to the raw motor calculations.

So the selection of correct amperage for a power supply still is
confusing. Since it works, I can't conmplian too much, but still
wonder if I am vastly over sized.

Hope that helps.

Dave

Discussion Thread

rllalonde2000 2005-01-26 04:28:01 UTC What size capacitor should I use? A. G. Eckstein 2005-01-26 04:58:31 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? Simon Arthur 2005-01-26 05:38:23 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? R Rogers 2005-01-26 06:56:31 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? Terrenoire, Adrien L 2005-01-26 07:00:14 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? Andy Wander 2005-01-26 07:01:23 UTC RE: [CAD_CAM_EDM_DRO] What size capacitor should I use? turbulatordude 2005-01-26 07:07:50 UTC Re: What size capacitor should I use? - voltage ? A. G. Eckstein 2005-01-26 07:13:30 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? caudlet 2005-01-26 08:00:51 UTC Re: What size capacitor should I use? Bengt 2005-01-26 09:11:26 UTC Re: What size capacitor should I use? Jon Elson 2005-01-26 09:28:27 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? Roy J. Tellason 2005-01-26 09:44:34 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? turbulatordude 2005-01-26 09:58:26 UTC Re: What size capacitor should I use? Andy Wander 2005-01-26 10:19:07 UTC RE: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? caudlet 2005-01-26 11:29:56 UTC Re: What size capacitor should I use? Roy J. Tellason 2005-01-26 11:41:56 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? Rob Polley 2005-01-26 11:43:12 UTC Looking for advice Dan Mauch 2005-01-26 12:18:29 UTC Re: [CAD_CAM_EDM_DRO] Looking for advice Codesuidae 2005-01-26 12:34:15 UTC Re: [CAD_CAM_EDM_DRO] Looking for advice victorlorenzo@y... 2005-01-26 12:55:47 UTC Re: Looking for advice Stephen Wille Padnos 2005-01-26 13:38:53 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? John 2005-01-26 14:04:29 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? Simon Arthur 2005-01-26 14:09:40 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? erie 2005-01-26 14:33:11 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? Stephen Wille Padnos 2005-01-26 14:37:28 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? R Rogers 2005-01-26 14:56:53 UTC [CAD_CAM_EDM_DRO] Toroidal transformer ratings?? Amps? Kv? Kva? JanRwl@A... 2005-01-26 15:04:42 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? Les Newell 2005-01-26 15:05:07 UTC Re: [CAD_CAM_EDM_DRO] Toroidal transformer ratings?? Amps? Kv? Kva? cnc_4_me 2005-01-26 15:08:24 UTC Re: What size capacitor should I use? David Paulson 2005-01-26 15:10:21 UTC Re: [CAD_CAM_EDM_DRO] Toroidal transformer ratings?? Amps? Kv? Kva? cnc_4_me 2005-01-26 15:23:15 UTC Re: Toroidal transformer ratings?? Amps? Kv? Kva? JanRwl@A... 2005-01-26 15:40:19 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? R Rogers 2005-01-26 15:49:48 UTC Re: [CAD_CAM_EDM_DRO] Toroidal transformer ratings?? What after being rectified? cnc_4_me 2005-01-26 15:55:58 UTC Re: What size capacitor should I use? cnc_4_me 2005-01-26 16:14:14 UTC Re: Toroidal transformer ratings?? What after being rectified? R Rogers 2005-01-26 16:18:19 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use?sizing supply Ron Ginger 2005-01-26 17:01:36 UTC Re: Looking for advice polaraligned 2005-01-26 17:09:38 UTC What size capacitor should I use? Polaraligned 2005-01-26 17:25:09 UTC Re: Toroidal transformer ratings?? Amps? Kv? Kva? R Rogers 2005-01-26 17:29:00 UTC Re: [CAD_CAM_EDM_DRO] Re: Looking for advice cnc_4_me 2005-01-26 18:05:05 UTC Re: What size capacitor should I use? victorlorenzo@y... 2005-01-26 18:19:00 UTC Re: Looking for advice codeSuidae 2005-01-26 18:32:59 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? cnc_4_me 2005-01-26 18:54:06 UTC Re: What size capacitor should I use? Ken Langston 2005-01-26 18:56:05 UTC Re: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? Amps? Kv? Kva? cnc_4_me 2005-01-26 19:01:47 UTC Re: Toroidal transformer ratings?? Amps? Kv? Kva? Rob Polley 2005-01-26 19:24:26 UTC Re: [CAD_CAM_EDM_DRO] Re: Looking for advice codeSuidae 2005-01-26 19:26:51 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? cnc_4_me 2005-01-26 19:35:49 UTC Re: Looking for advice bobmcknight@c... 2005-01-26 19:37:07 UTC Re: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? Amps? Kv? Kva? bobmcknight@c... 2005-01-26 19:37:08 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? cnc_4_me 2005-01-26 19:54:55 UTC Re: What size capacitor should I use? turbulatordude 2005-01-26 19:57:22 UTC Re: What size capacitor should I use? resistors.... cnc_4_me 2005-01-26 20:08:00 UTC Re: What size capacitor should I use? resistors.... JanRwl@A... 2005-01-26 21:34:22 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? JanRwl@A... 2005-01-26 21:43:19 UTC Re: [CAD_CAM_EDM_DRO] Toroidal transformer ratings?? Amps? Kv? Kva? codeSuidae 2005-01-26 21:56:30 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? Jon Elson 2005-01-26 21:56:33 UTC Re: [CAD_CAM_EDM_DRO] Toroidal transformer ratings?? What after being rectified? Mariss Freimanis 2005-01-26 21:58:04 UTC Re: What size capacitor should I use? resistors.... Jon Elson 2005-01-26 22:08:03 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? JanRwl@A... 2005-01-26 22:09:14 UTC Re: [CAD_CAM_EDM_DRO] Re: Looking for advice Jon Elson 2005-01-26 22:22:35 UTC Re: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? Amps? Kv? Kva? Jon Elson 2005-01-26 22:29:43 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? resistors.... Jon Elson 2005-01-26 22:33:41 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? resistors.... Simon Arthur 2005-01-27 00:01:53 UTC Re: [CAD_CAM_EDM_DRO] What size capacitor should I use? Polaraligned 2005-01-27 04:15:31 UTC Re: What size capacitor should I use? Polaraligned 2005-01-27 04:29:29 UTC Re: Toroidal transformer ratings?? What after being rectified? turbulatordude 2005-01-27 06:26:30 UTC Re: What size capacitor should I use? resistor or not ?? turbulatordude 2005-01-27 06:45:41 UTC Re: Toroidal transformer ratings?? What after being rectified? Leslie Watts 2005-01-27 07:04:52 UTC RE: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? What after being rectified? Jon Elson 2005-01-27 10:30:37 UTC Re: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? What after being rectified? Jon Elson 2005-01-27 10:40:20 UTC Re: [CAD_CAM_EDM_DRO] Re: What size capacitor should I use? resistor or not ?? cnc_4_me 2005-01-27 10:47:17 UTC Re: Toroidal transformer ratings?? What after being rectified? Les Newell 2005-01-27 12:49:45 UTC Re: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? What after being rectified? Polaraligned 2005-01-27 13:39:18 UTC Re: Toroidal transformer ratings?? What after being rectified? Stephen Wille Padnos 2005-01-27 14:44:25 UTC Re: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? What after being rectified? Polaraligned 2005-01-27 18:13:16 UTC Re: Toroidal transformer ratings?? What after being rectified? Steve Stallings 2005-01-27 18:18:44 UTC Re: Toroidal transformer ratings?? What after being rectified? Stephen Wille Padnos 2005-01-27 18:28:46 UTC Re: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? What after being rectified? Jon Elson 2005-01-27 21:35:23 UTC Re: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? What after being rectified? Kevin Martin 2005-01-28 05:32:28 UTC RE: [CAD_CAM_EDM_DRO] Re: Toroidal transformer ratings?? What after being rectified? m0nkey0ne 2005-01-28 11:22:47 UTC Re: Toroidal transformer ratings?? What after being rectified? Mcginnis, Darrell S 2005-03-22 14:43:20 UTC RE: [CAD_CAM_EDM_DRO] What size capacitor should I use?